Went to a customers house to diagnose a boiler fault. The above boiler isn't firing, there's no room stat. Tried running the hot tap. Tried re-setting it. Not even the pump is firing. There IS power to the boiler.

I've had a look at the ariston fault finding flow chart. It's looking like a new pcb will be needed. Is there anything else I could've missed before ordering a pcb? My friend who is GSR will be fitting it as I'm not registered until next month.

thanks in advance.

Dom.
 
before looking at a pcb check the basics you dont say if you have checked fast fuses or the lwp
 
Hi, I visually checked the fuses, couldn't see any signs of burning out.
 
the ariston pressure switch is set to 1 bar... make sure the pressure is 1.5 bar.... check if power is getting to the fan, may be the fans knacked too, did you hear the pump if not the sounds like fast blow fuse as gasman said or PCB.
 
Hi Yes, I checked the pressure as he mentioned in the past it has tripped out. It was over 1.5 bar. Are the fast blow fuses pcb specific?
 
the ariston pressure switch is set to 1 bar... make sure the pressure is 1.5 bar.... check if power is getting to the fan, may be the fans knacked too, did you hear the pump if not the sounds like fast blow fuse as gasman said or PCB.

also you need to bear in mind the lwp(low water pressure switch) may be knackered,its a 2 wire circuit loop them together to verify but do not under any circumstances forget to unloop them and leave the boiler working like this
 
Just a quick update. Turns out it was the LWP switch, so I'll be picking one up tomorrow and getting it fitted. Thanks everyone for your helpful replies :)
 
Just a quick update. Turns out it was the LWP switch, so I'll be picking one up tomorrow and getting it fitted. Thanks everyone for your helpful replies :)

so you have learned.......loads always check the basics glad its sorted mate
 
Hi, forgot to update this, ordered a new switch, drained boiler, replaced switch and filled boiler then turned it all on, still not firing. So thought I'd just try bridging the switch again, and boiler fired straight away. Surely I havn't got a new faulty switch. I was wondering if there could be some sludge/dirt in the pocket the switch sits in? Maybe worth flushing through? Or have I missed something glaringly obvious?
 
try taking out and cleaning also check where it screws in for a blockage
 
If the lwp has 3 electrical connectors, are the wires connected to the correct terminals ?
 
it would not make any difference as it just makes once the pump comes on, you will probably find there is dirt in it again, bad design really that a match head of crud can stop a boiler but that what keeps us in business and drives us round the bend sometimes lol
 
and you have probably tried swapping them around ?

Yes, will go and give it a clean tomorrow. It's a secondary boiler in a loft conversion, so they're still nice and warm as they have a different boiler running the rest of the house.

Cheers for replies guys.
 
it would not make any difference as it just makes once the pump comes on, you will probably find there is dirt in it again, bad design really that a match head of crud can stop a boiler but that what keeps us in business and drives us round the bend sometimes lol

your thinking of the microgenus this has a pump pressure switch,no lwp the microcombis different twinpass heat exchanger and it has a lwp but no pump pressure switch ,but as i posted earlier i agree on crud back in the lwp,or were it screws in to the flow pipe
 
my mistake ,yes like the puma i suppose ,i will get the hang of these boilers someday lol
 
yes I make you right there and i forget whats what and should keep notes which i may start doing soon , for example I went to change a fan on a keston c55 that cost loads ,only to think yes chop the wires of and remove fan fortunately I sussed they supply an extra wiring loom that extends and connects on the existing wiring loom if that makes sense, it would have been a nightmare if i had chopped the wires out
 
Update - Gave the prv area where the lwp sits a flush and clean out. All working fine. Thanks to all for the advice on this thread. I'm thinking about getting myself a little netbook and dongle so I can go straight online to download any boiler instructions I might need when working in the future.
 
Status
Not open for further replies.

Reply to Ariston Micro Combi in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
317
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock