Had polypipe underfloor heating installed around 4 years ago. Flow rate used to be around 2.5 l/m now its just over 1 l/m. Tiled floor now is heat patches
I have a nest connected to this also. And 3 zones come on at once in same port on slave unit

I've changed the pump, diverter valve and mixing valve with no change in performance. Also I've connected a hose for each of the 3 zones which I get 3 l/m. I don't know what else to do. Ay help?
 

Attachments

  • 20221019_143914.jpg
    20221019_143914.jpg
    258.3 KB · Views: 25
  • 20221019_143920.jpg
    20221019_143920.jpg
    189.5 KB · Views: 25
I think your pump is set wrong it’s on pressure instead of constant as the 3 lights arnt illuminated

Press and hold the setting button for 3 seconds then it should be on constant if the leds are flashing press and hold for another 3 seconds
 
I think your pump is set wrong it’s on pressure instead of constant as the 3 lights arnt illuminated

Press and hold the setting button for 3 seconds then it should be on constant if the leds are flashing press and hold for another 3 seconds
I did change that earlier. it's on cont curve 1.. the first 3 lights...
Been on cont curve for 2 hours with no difference
 
And the pump is correct eg pumping away from the mixing valve ?
 
That’s correct

And the old pump was a 15-60 ?
 
When I have underfloor heating on only the system boiler has a c and burner flashes. When I turn on central heating c comes on and burner light is solid. Boiler is icos 12he.
I assume its a circulation problem
 
I would say
 

Reply to Polypipe underfloor heating not heating up properly after a few years in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
295
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
141
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
209
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
344
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
246
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock