We have a 2 year old Valiant EcoTec 832 Combi boiler which was running our CH and hot water.

We recently had some UFH installed and the boiler moved to our new extension.

Over the past weeks the pressure in the heating system keeps creeping up. It goes from approx 1.5 to 3.2 bar overnight. If I do not drain any of the water out it remains at approx 3.2. When I drain the water to bring the pressure back down it creeps back up by the next day.

I have checked the filling loop valves and they are all in the off position.

One plumber suggested (over the phone) that we would need an expansion tank fitted as the pressure rise may be due to the installation of the UFH system?

Is this correct or is it more likely a fault somewhere?

Thanks!
 
As Brambles says above, fill to correct pressure, cap off filling loop to ensure the system isnt further filling and monitor over the course of a day or two.
It could very well be down to the expansion vessel charge or even sizing. With the additional UFH circuit/circuits being added you've increased overall system volume, which could have and often does result in the original vessel being undersized and not man enough for the job.
Really this should have been considered when designing these add ons
 
The other possibility is you have a split in the PHE coil causing cold mains pressure to reach into sealed system increasing the pressure that way if the vessel is sound and filling loop not letting by.
 
Sounds more like a filling issue to me rather than expansion.

As if it's a 1.5 bar goes up to 3.2 bar but then doesn't come back down when everything cools, if it was an expansion issue it should decrease at least when the heating is off.

If you're having to let the water out yourself it sounds like something is filling the system.....
 
Update: Emptied and re-adjusted the pressure on the expansion vessel which was very full of water!

Disconnected the filling loop hose to find that the valves on both sides were leaking! Capped for now and am monitoring. But so far it looks like the pressure is holding.

Will monitor for another 24-36 hours and report back.

Thanks all for the help!
 
Thanks,

Do you mean that water was exiting the expansion vessel from the Schrader air valve? If so, the vessel needs replacing.

Obviously the filling loop assembly and non return valve also need replacing.
 
Looks like you have two issues then, at two years old your boiler should be still under warranty. give them a call they are still coming out to warranty work.
 
The expansion vessel valve was fine - no water exiting. Since disconnecting and capping the filling loop valves the pressure has been stable.

The two valves either side of the filling loop were both leaking (cold water inlet valve and service cock).

have ordered replacement for both.

thanks for the help
 
The expansion vessel valve was fine - no water exiting. Since disconnecting and capping the filling loop valves the pressure has been stable.

The two valves either side of the filling loop were both leaking (cold water inlet valve and service cock).

have ordered replacement for both.

thanks for the help
The boiler not under warranty?
 

Reply to Pressure in heating system keeps creeping up in the USA area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
109
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
109
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
397
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
236
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
314
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock