Messages
22
Hello

I'm seeking helpwith a central heating problem please. It's a fully pumped system with a diverter valve for cylinder / rads and has an open header tank. Potterton Prima 40B.

The first sign of trouble was yesterday evening, no hot water. The hot water and radiators had been ok earlier in the day.
The pilot light was out so I easily re-lit it and turned the control valve back from the igniter setting to on. The main burner fired, job done I though, but it wasn't.

No hot water this morning.

The pilot lights easily and stays on if there is no demand for heating. The pilot flame looks like it's bathing the thermocouple. Once a demand is placed, the main burner fires immediately, then 10 to 60 seconds later there is a click and both the main burner and pilot are extinguished. This is repeatable. I can't see if the pilot flame is bathing the thermocouple correctly once the main burner fires, there is just too much light in there. I checked the thermocouple with an Avometer. Minimum scale is 3V so only millimetres needle movement however the reading is consistent with 20 mV. My DVM isn't at home and it'll take a couple of hours to get it. The pump is vibrating, so seems to be working.

I followed the fault finding chart in the instructions and it doesn't really cover this situation.

Anybody have any thoughts please?
 

Reply to Potterton Prima 40B cutting out - help sought in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, Later this year I am going away for a 2 week holiday and as the weather will be warm there is no need for the heating to be on and arguably no need for me to needlessly heat hot water. My intention was to turn the boiler off along with the mains water when going away. Now, I have heard...
Replies
1
Views
85
Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
147
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
359
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
484
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock