I live in Azerbaijan where I have a Wilo MC605-EM pump attached to a Wilo LRS 50/10H diaphragm expansion vessel, which pumps water into my house on demand. We have a large water storage tank sitting between the mains and the pump so there is effectively no water pressure, the pump sucks water out of the tank and pushes it into the house.

The meter on the pump outlet by the braided hose is reading 3.5 bar which I guess is just the pressure in the pipework until someone opens a tap.

The pump is misbehaving, going in short bursts of brrr-clunk-silence-brrr-clunk-silence and the water comes out of the taps in the house in bursts. As I understand it, I need to re-pressurise the expansion tank, but I can't find any good instructions on how to do that. I believe that if I don't do it soon it may damage the expansion vessel which I think has a butyl rubber diaphragm.

There's a label on the tank that just says "in case of insufficient air pressure please empty all water from the tank and replenish dry air by using a compressor". I do have an air compressor available.

The pump is connected by threaded fittings on the top and left of the picture. I can undo these easily enough, and that will drain the pump - but I think not the expansion tank as that sits underneath connected by a large braided hose. So how do I empty the water from the tank? And when I've done that, what pressure to I put back into the expansion tank?
 

Attachments

  • Pump.jpg
    Pump.jpg
    90.5 KB · Views: 7
Last edited:
may have split so might need replacing there should be a schrader valve in the opposite end to the flexi might be a cap on it when you press the core in do you get water out or air?

to recharge with air

turn off the suply to the pump (electric)

then turn off the supply to the pump (water)

open the cold tap / item down stream of the pump

there should be a data plate on the expansion vessel to give you pressures

to recharge you just need a bike pump and pressure gauge
 
The label says:
The proper air pressure must be:
  • in booster systems p0 = 0.9 x pmin
  • in heating systems p0 = ps + 0.2bar
  • in cooling systems p0 = ps

p0 = air pressure (bar)
ps = static water pressure (bar)
pmin = start-up pressure (bar)

And in a separate box that is like the tank characteristics:
  • Operating pressure pmax = 10 bar
  • Test pressure ptest = 15 bar
  • Preset air pressure p0 = 1.5 bar

I'm kinda lost there....is the answer just 1.5 bar?

But unfortunately, water came out of the Schrader valve, so it looks like I have a split in the membrane. Is this repairable, or do I need to replace the whole expansion tank? There's a flange at one end, can you unbolt that and swap out something inside? I'd be happy to have a go at that if I can get the parts. Do the bolts need tightening with a torque wrench?

This isn't the first time that this has happened, I think the second in about 5 years. What causes this, am I doing something wrong? Or more likely, not doing something I should? How often should I check the air pressure? I have another two stand-alone expansion tanks in my hot water system, both larger than this. I don't really understand what they do...but the heating system is something for another thread!

Many thanks...
[automerge]1580894297[/automerge]
I'm kinda lost there....is the answer just 1.5 bar?
And if so, what's the significance of the 3.5 bar reading on the dial? Isn't this also the pressure in the expansion tank?

Meantime, have asked Wilo Azerbaijan about spares...
[automerge]1580912878[/automerge]
OK, I bought a new bladder, about £10, and have a much better idea of what's going on, thanks to YouTube
View: https://www.youtube.com/watch?v=2NMdjft_Ces

View: https://www.youtube.com/watch?v=NPZw83Iypzg


So now I understand that I need to put 1.5 bar into the tank after fitting the new bladder.

When pressurising the tank, the house it's connected to is 3 storeys so there's a head of water in the pipework of about 12 metres. So it seems to me that it's better to isolate the upstream pipework and disconnect the pump to pressurise it. That's easy enough.

Many thanks for the tip to look for water in the valve, that helped a lot to understand what was going on.
 

Attachments

  • Flange.jpeg
    Flange.jpeg
    87.1 KB · Views: 4
Last edited:
I would say whole new pump unit is required
 

Reply to Wilo pump & expansion tank - need to repressurise in the USA area at PlumbersForums.net

Similar plumbing topics

Hi, I am currently using a Grundfos Booster Pump. This pump is fed by 2pcs of 1,000 liters water tank. Normally the pump would stop working only when there is no water in the water tank. But, recently for the past week, in the middle of the night, the pump would stop working even though the...
Replies
0
Views
185
My central heating is run off a heat pump ( air to water ) quite expensive to run , So I’m plainning to fit a wood burning with a back boiler to connect to the heating system, So while the wood burning on during winter months it will stop the heat pump for working hard Or not all all . My...
Replies
3
Views
235
    • Like
Hi there, I’m hoping someone can help me with this problem please. I’ve searched for similar posts but not found anything helpful! My mum’s house has a pump which pulses on and off every time a tap is opened. Even filling the bath (pressure is strong) the pump won’t come on and stay on but...
Replies
12
Views
517
Good afternoon, I am experiencing a pressure issue with my heating system and was hoping to receive additional insight as to what the problem could be. We have a biomass boiler and stratification tank set up and recently had an issue with boiler pressure dropping off when the system was cold...
Replies
9
Views
342
hello we have an unvented system. we have an issue where the hot water is hot for 10 seconds and then luke warm, turn off taps / wait and turn back and it repeats itself. had boiler checked and told it was the expansion vessel. Had the expansion vessel drained and recharged. plumber told me...
Replies
5
Views
671
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock