This may be just the part of the world I'm in but I can't remember in my working life, seeing an oil tank inside a property before. ( commercial property) I know it's allowed but there are rules.
This one is face to face with the boiler ( 2 foot max away).
steel tank, no bund, no fire chamber/compartment, no ventilation I can see and no fire valve !

has anyone else seen the like ?
 
Last edited:
Yes. Worst one I know is a bungalow with garage at end. Small metal oil tank of about 1100 litre just above the boiler on purpose built walls in rear of garage. Been like that from the 1960s.
 
Yes. Worst one I know is a bungalow with garage at end. Small metal oil tank of about 1100 litre just above the boiler on purpose built walls in rear of garage. Been like that from the 1960s.

Sounds a similar sized tank.
The burner needs a new pump but it's around half price of a new burner.

If I end up replacing the burner I'll fit a fire valve, new filter and oil line but what about the tank installation?

It's been in for donkeys years but should it be updated
i.e. Is it a legal requirement or a recommendation
 
Last edited:
I am guessing, - but think that oil tank should be removed.
Contact OFTEC and ask them what the regs will be. Croppie should also know as he does commercial.
Any work you do obviously should be done with plenty of paperwork to state oil tank is a danger. Personally, I wouldn't do any work to the boiler until I spoke to OFTEC and building control
 
Recommendation only unfortunately. Document it and cover your a$$ that's all you can do. Last one to touch is responsible.

Probably 95% of the oil tanks I visit don't meet the current regs. Must cost me an extra box of biro's.

'Customer advised :- blah blah blah'
 
Day tanks should have all kinds of features including the bund.

The most important one is a fire valve which opens in the event of a fire and dumps the oil back into the main tank.
 
one wonders if anyone working on oil is oftec qualified and know the rules judging by the questions asked at times
 
Day tanks should have all kinds of features including the bund.

The most important one is a fire valve which opens in the event of a fire and dumps the oil back into the main tank.

Thanks for that Croppie but This isn't a day tank it's the main oil tank.
Emailed Oftec today cos phone line busy.
No reply as yet.
 
Yes I have a customer with a steel tank in a garage with the boiler alongside it. Its been there for about 40 years. Customer knows if anything needs to be upgraded then a compartment will have to be constructed which means the garage would have to be sacrificed meaning nowhere to put the car (there is no drive as it is directly onto the road and there are double yellow lines along the street, and there is no garden to put the tank in as an alternative). Another customer once had a boiler and tank next to each other in a hay store next to a stable. That was the first job I was asked to sort as their insurance company did a survey when the bought the property.
 
Regardless of the OFTEC regs, if its a commercial installation then the owner has additional responsibilities under the HASAWA and various Fire Safety Regulations.
They have a statutory duty to ensure that risks to their employees and members of the public are as low as is reasonably practicable.
Installing a new tank and a fire valve seems very reasonable to me.
Saying it was kosher when it was installed wouldn't stand up in court if there was a fire.
 
Regardless of the OFTEC regs, if its a commercial installation then the owner has additional responsibilities under the HASAWA and various Fire Safety Regulations.
They have a statutory duty to ensure that risks to their employees and members of the public are as low as is reasonably practicable.
Installing a new tank and a fire valve seems very reasonable to me.
Saying it was kosher when it was installed wouldn't stand up in court if there was a fire.

I agree. Spoke to OFTEC Tech. Pretty much what I thought and what a few before said.
Document it, advise the owner etc.

There have always been rules regs and plain common sense where things like this are concerned. If I had seen it 30 years ago, I would have thought it a bad installation and its not something I would have ever done myself.
 
Status
Not open for further replies.

Reply to Internal oil tank in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
300
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
229
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
365
I was stupid enough not to check the position of the pipes under the tiles when installing a toilet and drilled right through the center of a 16 mm copper water pipe. I exposed the pipe by removing a ~30cm section of the plastic sleeve and a ~10 cm section of the pipe around the hole. Several...
Replies
0
Views
168
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock