Ideal logic plus 30 kw, gas rated at 21 kw net on hit water. Inlet pressure 21mb at boiler, flow rate 12 lit pm, temp 40.3 degrees. Have checked, gas valve, injectir internal boiler pipework for blockages. Fga readings fine, boiler gas rate on central heating 23.5 kw net, service mode gas rate spot on. Any ideas please, the hot water is not as hit as ut was. Diverter ok, plate fine
 
Ntc ok / readings somewhere near ?
 
Im

I dont think thete is a hw thermister, can check the flow and returns thermisters. I take it the gas input is not directly related to the flow turbine speed, can anyone explain how the hot water side works in relation to the gas valve and fan speed??
 
Flow turbine has big say in gas being burnt as it gives flow rate signal to pcb via hall sensor.
How old is boiler as turbines can get a bit cruddy depending on location after a couple/few years meaning hall sensor info to pcb may be out thus lower gas rate on DHW.
You may be able to clean up a bit once removed but does not last forever.
I usually change the turbine & job done,
Cheers,
Andy
 
if you've got the logic plus turn hot tap on full and leave it on. then turn mode switch to reset position and hold it there for a few seconds and boiler will go into installer mode burner will go off but will relight display will now scroll through last ten faults then display current parameters. flow temp, return temp.... and will then show dhw flow rate in L/min which turbine is registering to pcb. if this is lower than your reading from a combi cup or other device tbh your better changing the turbine than trying to clean it. also look at the red light on the hall sensor is it a steady red light or flickering, if flickering turbine on way out
[automerge]1576802639[/automerge]
if you've got the temp clamps for your analyser put one one on flow and one on return from main hex to check temp diff across plate. hw out should read approx same as return temp if plate not blocked and circulating properly
[automerge]1576803073[/automerge]
best way to check max gas rate is to turn heating on then put boiler into service mode high then it runs the full 30k into the radiators and eliminates poor hot water fow
[automerge]1576826104[/automerge]
bit i missed off first post. after turning tap on turn both hw and ch to minimum settings then hold mode switch in reset for a few secs. when boiler goes into installer mode then turn hw back to max. rest as above
 
Last edited:
Thanks very much all, about a month ago the hot water was playing up, hall sensor flickering. I took out the flow turbine and cleaned it up and all was good or so i thought. Hence a new flow turbine is required. How come Ideal coundnt tell me that when i phoned them??
 
Thanks very much all, about a month ago the hot water was playing up, hall sensor flickering. I took out the flow turbine and cleaned it up and all was good or so i thought. Hence a new flow turbine is required. How come Ideal coundnt tell me that when i phoned them??
all boiler manufacturers tech helplines are only good up to a certain point. if you really want to know you need to find your local engineers from different manufacturers who work on these every day and try and get their number if possible. an awful lot will be willing to help if they can of course you will get the occasional miserable bugger who says its not my job
 
Flow turbine has big say in gas being burnt as it gives flow rate signal to pcb via hall sensor.
How old is boiler as turbines can get a bit cruddy depending on location after a couple/few years meaning hall sensor info to pcb may be out thus lower gas rate on DHW.
You may be able to clean up a bit once removed but does not last forever.
I usually change the turbine & job done,
Cheers,
Andy
no point in trying to clean it if not spinning properly just change it as you said
 
Ideal logic plus 30 kw, gas rated at 21 kw net on hit water. Inlet pressure 21mb at boiler, flow rate 12 lit pm, temp 40.3 degrees. Have checked, gas valve, injectir internal boiler pipework for blockages. Fga readings fine, boiler gas rate on central heating 23.5 kw net, service mode gas rate spot on. Any ideas please, the hot water is not as hit as ut was. Diverter ok, plate fine

What was the incoming cold water temp? i.e. what was your temp rise?
 

Reply to Ideal logic 30 low gas rate in the Gas Engineers Forum area at PlumbersForums.net

Similar plumbing topics

Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
192
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
230
My son has an apprenticeship interview for to become a plumber and heating engineer. The have said there will be a multiple choice exam for this for suitability. The thing is my son panics during tests/exams. Is there any book I can buy him to practice the multiple choice test for the exam? What...
Replies
3
Views
273
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
2
Views
136
I have a plumber coming tomorrow to change a cartridge on a badly dripping tap on my bathroom mixer unit. There is no separate isolating valve for this tap so I'll have to close the stopcock. I tried closing it today but it won't go absolutely 100% closed and there is still a very slight flow...
Replies
1
Views
186
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock