whats the best wiring to use for underfloor heating stats. I'm hardwiring it all. Not wireless.

Thanks
 
At least 3 (eg 3 core twin and earth ) but depends on stat
 
Know nothing about U/F controls ! but would have thought 4 core , L/N/E & switched L , people do this on other heating controls and finish up using 'N' for switched L then it gets confusing back in the wiring centre
 
Most people take the easy route and use a 5 core 1mm flex, it gives you one spare core, and is easier to install at the controller end when you've got 8 room stats coming back to the one controller.

Of course it depends upon the make and model of the room stat / programmer, some are 12V, some 230V some send back a switched live some have a pair of zero V contacts. Some of the 12V ones run happily on Cat6 or Belden 9538

Now, how long was that piece of string?
 
Last edited:
Know nothing about U/F controls ! but would have thought 4 core , L/N/E & switched L , people do this on other heating controls and finish up using 'N' for switched L then it gets confusing back in the wiring centre
L,N,s/L and earth is called three core.:sosp:
 
L,N,s/L and earth is called three core.:sosp:

OP may not know that, average person only see 3 or 4 inner wires so will call it 3 core etc. where people in the trade tend to use twin & earth etc. (3 core) gets confusing for Mr average !!
 
OP may not know that, average person only see 3 or 4 inner wires so will call it 3 core etc. where people in the trade tend to use twin & earth etc. (3 core) gets confusing for Mr average !!

It's not 3 core as the cpc can't be used as a live core
 
It's not 3 core as the cpc can't be used as a live core

The challenge is Sparks refer to three insulated cables plus the uninsulated cpc as 3 core :)
They are just lazy and forget to add the word earth to 3core and earth :)
Think of T&E = twin and earth
 
The challenge is Sparks refer to three insulated cables plus the uninsulated cpc as 3 core :)
They are just lazy and forget to add the word earth to 3core and earth :)
Think of T&E = twin and earth

yea but he said inner wires not cores :D
 
Status
Not open for further replies.

Reply to How many core wire for ufh stats? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We have an all Vaillant setup - an EcoTEC Plus 637 system boiler plus wired VR720 and VR92 SensoCOMFORT controller, driving two CH zones plus DHW. It all works, but unfortunately we have found that the room stats are poorly located, and so the level of control is not what it should be. We had...
Replies
4
Views
549
Hi, I am trying to link a Hive heating & hot water dual channel receiver to an old Vaillant THERMOcompact VU GB 242/1 E system boiler. It has an internal programmer that is similar to a time switch 120 (plug in seven day programmer) This programmer is connect to a terminal strip using 345 (three...
Replies
0
Views
403
Hi all. I've currently got a system boiler with cylinder and rads on s-plan. I'm planning on installing UFH in my kitchen/diner and utility/downstairs loo. My question is around mixing valves and opentherm. Do mixing valves dynamically adjust the amount of cold being mixed in response to the...
Replies
3
Views
340
Hi, I live in a really remote part of the Highlands, so paying for a plumber (or electrician?) to do this will be brutally expensive, so I need to do it myself. I have a Grant Combi 26e boiler. I'm replacing the old thermostat with a new one. Although the boiler is a combi, I think the old...
Replies
2
Views
537
Hi guys, I have a fault on a clients heating system whereby the heating will stay on regardless of what the programmer is doing on its timed function, it'll switch off at the programmer (no light) but boiler will stay on until they turn the stat down, I went and looked at it, they said they...
Replies
14
Views
2K
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock