i seriously wonder why they dont do two ports with unions. would make life so much easier
3 port 22 mm will pass 20KW
3 port 28 mm will pass 30KW
2 port 22mm will pass 23KW
2 port 28mm will pass 30 KW
yes all the above came from honeywell tech 2 weeks ago, when I queried it!
Lol Billy, mid pos always spilt 70/30 heating to hot water they are not 50/50 as mid pos would suggest lol*grins*
but with the three port i bet it will only pass 10/15kw each way when both sides are in use !!!
3 port 22 mm will pass 20KW
3 port 28 mm will pass 30KW
2 port 22mm will pass 23KW
2 port 28mm will pass 30 KW
yes all the above came from honeywell tech 2 weeks ago, when I queried it!
Post em up Roger, this was 2 weeks ago when I got through eventully! I queried the guy on Delta t and pump volocity etc, he went quiet, but pulled these figs from his PDFDifferent from the levels specced in there training manual.
ahhh !!! never knew that
so more like 14kw for heating, 6kw for hot water on a 22mm
21kw for heating and 9kw for hot water on 28 mm
pretty much means a 3 port isn't suitable for a megaflow or oso cylinder then !!!!
I was once told the rest or europe and the US use two port only and 3 port are (or were originally) made just for the UK because it's cheaper and consumers in this country always want a cheap job.
I find it believable. I bet northern europe, the US and canada would turn their noses up at a 3 port valve.
ahhh !!! never knew that
so more like 14kw for heating, 6kw for hot water on a 22mm
21kw for heating and 9kw for hot water on 28 mm
pretty much means a 3 port isn't suitable for a megaflow or oso cylinder then !!!!
Using a 3 port valve with any unvented cylinder is pointless, as you have to have a 2 port valve as well. This is to stop the cylinder been heated when the pump over run is in operation.
Using a 3 port valve with any unvented cylinder is pointless, as you have to have a 2 port valve as well. This is to stop the cylinder been heated when the pump over run is in operation.