Discuss Glow.worm boiler explosion. in the Central Heating Forum area at PlumbersForums.net

Messages
11
My LPG Glow.worm Ultracom 30 sxi boiler has exploded in some way. The front has blown open and the casing has buckled. (I was on holiday at the time. Thermostat left set at 16deg.) Annual Service four weeks ago. Boiler and heating still working! Any suggestions on cause?
 

Attachments

  • 9E056C27-C2A8-458D-AECF-053F8A21C80D.jpeg
    9E056C27-C2A8-458D-AECF-053F8A21C80D.jpeg
    124.7 KB · Views: 58
Turn it off and leave it off also time for a new boiler sorry to say
 
Thanks. Guessed that would be the case. Just wondered what could have happened especially as advised by engineer at service it was in excellent nick!

Have they every cleaned inside the boiler eg stripped it down ?
 
I’m guessing it didn’t light first time and when it fired the second the extra gas made it go bang maybe
 
I hope they replaced the burner door seal and nyloc nuts when they cleaned the hex & burner as required, & LDF the GV inlet. This as previously mentioned needs turning off, isolating and reporting to gas safe & riddor for investigation. DO NOT USE!
[automerge]1574760104[/automerge]
I’m guessing it didn’t light first time and when it fired the second the extra gas made it go bang maybe

Still it should not go bang even if it does not light first time. Should just go to lock out after 5 failed attempts should it not?
 
There are a number of reasons that could have happened and they may be unrelated to the Engineer. It is important you have this investigated for obvious reasons. There are others with the same Boiler, so if there is a fault it needs to be dealt with very soon.
Thank you. Have requested an engineer assessment and will ensure it is followed up.
 
I hope they replaced the burner door seal and nyloc nuts when they cleaned the hex & burner as required, & LDF the GV inlet. This as previously mentioned needs turning off, isolating and reporting to gas safe & riddor for investigation. DO NOT USE!
[automerge]1574760104[/automerge]


Still it should not go bang even if it does not light first time. Should just go to lock out after 5 failed attempts should it not?
mains gas shouldnt but lpg is a different animal. as lpg is heavier than air and it may not for whatever reason have all been purged out of combustion chamber on ignition sequence and has sat in bottom of boiler waiting for an ignition source
[automerge]1574797740[/automerge]
I hope they replaced the burner door seal and nyloc nuts when they cleaned the hex & burner as required, & LDF the GV inlet. This as previously mentioned needs turning off, isolating and reporting to gas safe & riddor for investigation. DO NOT USE!
[automerge]1574760104[/automerge]


Still it should not go bang even if it does not light first time. Should just go to lock out after 5 failed attempts should it not?
I hope they replaced the burner door seal and nyloc nuts when they cleaned the hex & burner as required, & LDF the GV inlet. This as previously mentioned needs turning off, isolating and reporting to gas safe & riddor for investigation. DO NOT USE!
[automerge]1574760104[/automerge]


Still it should not go bang even if it does not light first time. Should just go to lock out after 5 failed attempts should it not?
mains gas shouldnt but lpg is a different animal. as lpg is heavier than air and it may not for whatever reason have all been purged out of combustion chamber on ignition sequence and has sat in bottom of boiler waiting for an ignition source
 

Reply to Glow.worm boiler explosion. in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
207
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
283
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
212
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
188
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock