Hi all,

my employer took on a new build property which was built for them last year. There are 4x 480KW Ideal condensing boilers installed to serve a district heating network serving approx. 560 student apartments.
Due to a lack of decent control, these boilers are achieving a seasonal efficiency of circa 65%. Are there any minimum legally required seasonal efficincies for commercial condensing boiler plant rooms? I need to know so we can challenge the installer effectively that’s all.

Thanks in advance for any help.
 
Who did the design spec for the building and has it been done to spec if yes fault with the m and e designer no it’s not to spec m and e contractors

Will be listed in the m and e spec approx efficiency

I maxes ?

But tbh it’s not too bad since it’s summer
 
Who did the design spec for the building and has it been done to spec if yes fault with the m and e designer no it’s not to spec m and e contractors

Will be listed in the m and e spec approx efficiency

I maxes ?

But tbh it’s not too bad since it’s summer

Yes Imax boilers. The district heating network provides hot water on demand for the flats too via the plate heat exchangers in the houses (8 student bedrooms per house).

Efficiency is currently 50% through the Summer rising to 70% in Winter, I'd be better getting the engineers to rip out the old cast iron boilers that are due for replacement and fit them in our new build instead to be honest..
[automerge]1596746241[/automerge]
Yes Imax boilers. The district heating network provides hot water on demand for the flats too via the plate heat exchangers in the houses (8 student bedrooms per house).

Efficiency is currently 50% through the Summer rising to 70% in Winter, I'd be better getting the engineers to rip out the old cast iron boilers that are due for replacement and fit them in our new build instead to be honest..

We think the designers are at fault, the question I guess is what document do I use to hold them to account? Minimum seasonal efficiencies must be written down somewhere in British Standards etc, problem is I'm not sure where!
 
Floor mounted eg the xtras?

What’s the ratios like should be around 0.0002-0.0003

Eg they have been commissioned?

It’s around 90% Efficiency required
 
Your answer is in Here.
It can be complicated. I would start reading at the Bottom three.
All the things you need to find are in there but You'll need plenty of time.
As always, there are sometimes more questions created than answered.
 
Your answer is in Here.
It can be complicated. I would start reading at the Bottom three.
All the things you need to find are in there but You'll need plenty of time.
As always, there are sometimes more questions created than answered.

no link mate? / broken
 

Reply to Commercial Boiler Install Minimum Efficiencies in the Commercial and Industrial Plumbing Forum area at PlumbersForums.net

Similar plumbing topics

Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could be causing this leak. Already Changed the Pump Elbow as one of the clips had popped which was causing a second small leak, Any idea? Is it time to buy...
Replies
0
Views
204
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
253
My son has an apprenticeship interview for to become a plumber and heating engineer. The have said there will be a multiple choice exam for this for suitability. The thing is my son panics during tests/exams. Is there any book I can buy him to practice the multiple choice test for the exam? What...
Replies
3
Views
356
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
150
Hi guys. I'm trying to identify a toilet model before ordering a seat for a customer. I went to what used to be a Roca stockist (they no longer are) and one of the guys there reckoned it might be "The Gap". I went to the new stockist and the guy there disagreed it was "The Gap" and that he'd...
Replies
2
Views
112
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock