Hi all,

I have to balance radiators for some friends and whilst I've done plenty of other jobs for them this will be a first time effort! Does anyone have any tips or links to websites that show you what to do? Many thanks!
 
you will need clip/strap thermometers to fit to the flow and return pipework below the valves on each rad. you need to adjust the lockshield valve until you get a 10 degree difference in temp.
start with the rad closest to the boiler and work your way round.if they have a condensing boiler it will be about 20 degree difference

KJ
 
you will need clip/strap thermometers to fit to the flow and return pipework below the valves on each rad. you need to adjust the lockshield valve until you get a 10 degree difference in temp.
start with the rad closest to the boiler and work your way round.if they have a condensing boiler it will be about 20 degree difference

KJ



i would suggest starting from the furthest away from the boiler, as this one has more of the main circuit on it
 
Here is the guide I followed, the chart is very useful and I had it all balanced in 4 runs around - 10 rads took about 90mins.

UK DIY FAQ

Do yourself a favour and get a infrared thermometer, made it a doddle. Just put matt tape on the pipe and sweep the gun across a few times to get a consistant temp. mine was £19 on chavbay.
 
A quick simple way is to find out which is the first on the circuit(the first that gets the heat). If it is only over 1 floor then open the rads in order that they heat up(usually clockwise or anti-clockwise). If it over 2 floors then open the top floor by about a quarter turn and the lower floor by about half a turn.
 
Here is the guide I followed, the chart is very useful and I had it all balanced in 4 runs around - 10 rads took about 90mins.

UK DIY FAQ

Do yourself a favour and get a infrared thermometer, made it a doddle. Just put matt tape on the pipe and sweep the gun across a few times to get a consistant temp. mine was £19 on chavbay.


was it yourself that putthis on first time around?? as it was very useful to me and makes life much easier!! if so good man yourself!
 
It was me I think, I've posted it in a couple of places so far :)

glad it helped, I changed the spreadsheet to suit my needs, but its handy indeed.
 
Status
Not open for further replies.

Reply to Can anyone help with radiator balancing please? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello plumbers in my internet. So the Mrs want a spray mixer tap in the kitchen as we had two separate taps. I changed the tap for a temporary two hole mixer but the cold water pressure is high mains fed and the hot is low pressure immersion tank fed. I've been trying to find info on what I...
Replies
2
Views
69
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
95
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
212
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
135
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
91